Home electrical question
#2
What size shower do you have , if its 9kw or bigger , then it should be wired in 10mm cable , it is quite common for the pull switches to burn out , it is good practice to switch them off when not in use , as it reduces the chance of them arching out .
Rather than use a standard 30A junction box , get a 150mm by 150mm plastic adaptable box from an electrical wholesaler , and get 50A rated terminal blocks , just make sure the junction box is accessible for future inspection , i would preferably use through crimps if you have a suitable crimping tool .
Reply


Messages In This Thread
Home electrical question - by HarryHornby - 31-08-15, 10:57 AM
Re: Home electrical question - by esetest - 31-08-15, 11:17 AM
Re: Home electrical question - by fazersharp - 31-08-15, 12:56 PM
Re: Home electrical question - by HarryHornby - 31-08-15, 01:13 PM
Re: Home electrical question - by fazersharp - 31-08-15, 01:25 PM
Re: Home electrical question - by HarryHornby - 31-08-15, 01:39 PM
Re: Home electrical question - by fazersharp - 31-08-15, 01:44 PM
Re: Home electrical question - by Grayo - 31-08-15, 01:45 PM
Re: Home electrical question - by HarryHornby - 31-08-15, 02:58 PM
Re: Home electrical question - by Grayo - 31-08-15, 03:04 PM
Re: Home electrical question - by HarryHornby - 31-08-15, 03:06 PM
Re: Home electrical question - by fazersharp - 31-08-15, 03:12 PM
Re: Home electrical question - by esetest - 31-08-15, 03:14 PM
Re: Home electrical question - by HarryHornby - 31-08-15, 03:16 PM
Re: Home electrical question - by esetest - 31-08-15, 03:27 PM
Re: Home electrical question - by Grayo - 31-08-15, 03:28 PM
Re: Home electrical question - by fazersharp - 31-08-15, 03:32 PM
Re: Home electrical question - by esetest - 31-08-15, 04:01 PM
Re: Home electrical question - by HarryHornby - 31-08-15, 04:05 PM

Forum Jump:


Users browsing this thread: 1 Guest(s)