Any Sparkies? Lighting circuit question...
#7
maximum current carrying capacity for a 1mm cable reference method c  is 13.5 amps , so depending on how many other lights are on the circuit  you should be ok with 1mm , as the work is in a kitchen which is a special location so is notifiable , before altering the circuit you also need to make sure the circuit is protected by an rcd with 30mA protection , and the equipotential earth  bonding to the gas & water pipes is at least 10mm , i would recommend jcc  fire rated downlights as the lamps aren,t exposed , and are less likely to be a hazard if combustible material is nearby .  if you are involving building control they will want to see a certificate .
if your kitchen burnt down , and your asked if you have had any electrical work done and cannot produce a certificate , the insurance company may not pay out or reduce the payment .
Reply